Hello,
I just recently flashed a L7 processor from version 20 to version 32 and my sercos card is flashing the green ok status LED. When i go into module properties it says it is in "Program Mode" Help would be appreciated
Welcome to the PLCTalk forum community !
Did you also update the firmware in your 1756-M08SE SERCOS motion module ? In general, motion modules need to match the firmware of the controller, and version 32.001 is available for download for the 1756-M08SE.
Thanks Ken for the help,
And yes i did flash the module up to Version 32 as well. The ring light and the other status LED are solid green but the ok light is flashing. And i looked on rockwells forums and all they tell me is that the module is "not configured" which cant be true.
I would like the point out that the drives that i am controlling are in an off state at the moment for maintenance. Would this problem resolve itself once we boot those back up?
Again thanks for all the assistance
I believe you are correct that this will likely take care of itself when the drives are powered up. I suspect the SERCOS card is attempting to write parameters to and trigger phase transitions in drives that aren't responding. I wouldn't get too worried until the drives are available again.
Keith
We will be starting up soon and I’ll drop a follow up comment if this resolves the issues.
Thanks for all the help. It is very much appreciated.
Gentlemen,
I booted drives up and all issues were resolved. Thanks for the quick response and I definitely look forward to using this forum in the future.
"Do or Do not, There is no Try" -Yoda
Hi all, I'm new to this site but have been programming for a long time. I have a situation where I need to disable 1 of 2 1756-M08SE modules...
1,695
Hi all I have a ControlLogix 1756-L71SP that i want to use for general PLC applications, not safety. I am running Studio5000 v33, i can't...
81
388
Hi, I have two quick questions: 1- Could I use 1756-IA16/A with TTL inputs? Sourcing (PNP)? Sinking (NPN)? Either one? 2- What does /A in the part...
183
Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
156