Hi ,
I am using Prosoft communication module (MVI 56-MCM)MODULE.
I configured the port 1 for Modbus slave with RTU protocol.
Communication link is on RS232C cable connected to DCS via PHONIX CONTACT (serial to fibre optic convertor).
when connected to DCS link my port 1 LED is showing continous GREEEN.BUT DCs serail to fibre converter Tx and Rx not blinking green .they are Tx is blinking green and Rx is blinking Amber.
If data transmission is happening then as per manual it shold blink rapidily.
Onaly 2 cables are used in this transmission. transmit , recieve and ground.
RTS & CTS are jumpered.
Also where i should configure the MODULE internal write data block (DCS will read from this addresses) start address.
Also i can see the diffrent offsets for Bits and Integers to be written to internal data block.
How in program that i should tell the module that this is data is bit andthis is Integer.
hope some one can clarify me on this.
I am using Prosoft communication module (MVI 56-MCM)MODULE.
I configured the port 1 for Modbus slave with RTU protocol.
Communication link is on RS232C cable connected to DCS via PHONIX CONTACT (serial to fibre optic convertor).
when connected to DCS link my port 1 LED is showing continous GREEEN.BUT DCs serail to fibre converter Tx and Rx not blinking green .they are Tx is blinking green and Rx is blinking Amber.
If data transmission is happening then as per manual it shold blink rapidily.
Onaly 2 cables are used in this transmission. transmit , recieve and ground.
RTS & CTS are jumpered.
Also where i should configure the MODULE internal write data block (DCS will read from this addresses) start address.
Also i can see the diffrent offsets for Bits and Integers to be written to internal data block.
How in program that i should tell the module that this is data is bit andthis is Integer.
hope some one can clarify me on this.