I have a micrologix1500 connected with RS232 to my computer, and connected to the 1761-net-dni with a series connexion from the controller.

I would like to ask if I can configure the 1761-net-dni to be like a scanner, in order to communicate with a powerflex40 device net.

What is the configuration Ihave to do in order to have a DeviceNet with Rslogix500.

Regards.
 
The 1761-NET-DNI functions as a DeviceNet slave, as well as a peer-to-peer messaging bridge.

It is not a DeviceNet Scanner.

To control DeviceNet slaves, including variable frequency drives like the PowerFlex 40, your MicroLogix 1500 should be equipped with a 1769-SDN DeviceNet Scanner.
 
There are some tricky and unusual methods for sending Command and Reference words, and reading Status and Feedback words, from the MicroLogix 1500 to a PowerFlex 40 using a 1761-NET-DNI and the 22-COMM-D DeviceNet adapter option board.

But they are not easy to use, and I would not recommend them.

It would be a lot easier to configure the MicroLogix serial port for Modbus RTU Master mode, connect an RS-232/RS-485 converter, and wire that to the PowerFlex 40's "Drive Serial Interface" (DSI) port.
 
Hello
There is no way to add the PowerFlex only with the 1761-NET-DNI, that will be my slave and the master will be the micrologix?

Also is there any mean to add a devicenet to my micrologix? I used it before with rslogix5000 and I use RSNetworx.

Thank you.
 
>There is no way to add the PowerFlex only with the 1761-NET-DNI, that will be my slave and the master will be the micrologix?

That is correct. The 1761-NET-DNI is not a DeviceNet "Scanner" or "Master" device.

>is there any mean to add a DeviceNet to my MicroLogix?

Yes. The 1769-SDN is a DeviceNet Scanner modules that is compatible both with MicroLogix 1500 and with CompactLogix controllers that support the 1769 Compact I/O bus.
 

Similar Topics

Hi, Getting some hands on training and putting together a Micrologix 1100 trainer that that will be used to control DeviceNet DrIves and Valves. I...
Replies
8
Views
1,615
Hello Friends I need to communicate a 5/03 PLC with a Micrologix 1400, to send and receive some bits and integers between both PLCs. Int the...
Replies
3
Views
3,300
Hi ! I would like to know if it is possible to use a MicroLogix 1400 with a 1761-NET-DNI module AND Modbus RTU at the same time ? Thanks in...
Replies
14
Views
4,272
Hi friends I have followed the instructions in DeviceNet Interface User Manual Catalog Number 1761-NET-DNI page 69... But Heartbeat never...
Replies
0
Views
1,419
Hi everyone, i´ve done the little project and run perfectly. This is the practice in capture images. this is the first step, exchange I/O between...
Replies
2
Views
2,168
Back
Top Bottom