Hello, I would like to install a 1.25k-ohm potentiometer to a 1794-IE8. All I have is a 24VDC source. I noticed that the input ranges from 0-15VDC. Will this hurt the module? As I read this it looks like a silly question....maybe the heat? šŸ™ƒ
Try using a 250k ohm resistor on the wiper of the pot going to the PLC, this should drop the voltage down from 0-24 to 0-10ish
You need a 750 ohm from +24DC to the potentiometer and then voltage in the cursor will vary from 0 to 15V .
The total power dissipation will be V2 / R -> 0.29W
Also instead de 750ohm resistor you can use a 500ohm fixed resistor and a 500ohm trimmer potentiometer in series, then you can adjust exactly the 15VDC max. voltage in the main potentiometer
I do it all the time... but my pots are only 1k, thats where lfe got the 750 and mine are 250k
Thats also why I have a large bag of resistors that vary in size, I only use 1k pots so the math is easier :D
Dear Members; We have Fluke 754 hart communicator. We have wired up three transmitters of Rosemount Model C3051 with this input module. But when...
1,853
Hello all. I have a job to add a 1794-IE8 Card in slot 5 on an existing Flex IO Rack which uses a 1794-ASB communications module, which...
3,001
I am trying to scale an analog input for 4-20ma. Rockwell's website says that 0-30840 are the proper numbers. But the unscaled input raw is...
1,887
Hi All, I've probably programmed hundreds of 1794-IE8's over the years. The panel builder I'm working with has installed thousands of these so I...
2,331
Hi, I am using an Analog Input Module - 1794/IE8 My Analog Input Module is configured for 0-20mA Unscaled Max = 31208 Unscaled Min = 6241.6...
7,045