2 motors alternating on/off for 1 second
SP3000
Jan 2017
Canada
I have 2 motors on a VFD that are alternating on/off when started (HOA switch in auto) after an ESD. When the operator toggles the HOA switch from auto to hand and back to auto, the motors stop alternating on/off and run as they should (one at a time) any ideas on the cause?
Welcome to the forum. Maybe it's the time of day but I'm having a hard time tracking with you. Let's see if you can clear this up and help us help you:
1. Is it one VFD per motor or both motors connected to a single VFD? Please give some more detail on the overall physical connection picture.
2. What is the HOA switch wired to? Drive, PLC, etc.??
3. I'm guessing ESD is not electrostatic discharge. Can you clarify? I'm not sure of the relevance to the issue at this point.
4. Providing make/model info of any drives, PLC, etc. is never frowned upon and usually quite helpful.
That's enough for now...
Hi I'm kinda new at PLC programming sorta teaching myself. I need to alternate between two motors run one till satisfied the when it calls again...
1,520
Any help would be greatly appreciated! I have reached my final project in my PLC class with a teacher that doesnt know what hes doing so i have...
20
7,101
We have a used piece of water filtration equipment. Long story short, 2 motors/pumps that are currently on contactors. Pump1 needs to be sent...
41
20,640
Hello I have wrote a PLC code to alternate two motors each two hours, i.e. M1 operates for two hours then stops & M2 runs for another two hours...
1,725
I have been using a variable speed drive for every pump for our machines and had the idea of using 1 drive to alternate between 3 pumps, the other...
29
15,683