I have an analog input that is used as the PV to a PID.
The PID controls an analog out.
The analog out is connected to a transducer.
The PID is reading the input at just above zero and has ramped up the output to 100% .
The transducer does not respond. (the whole loop worked perfectly Friday. I do not think I made any changes today that would affect this loop.
The analog output connected to the analog out is supplying 4.8mA DC as indicated by a FLuke DMM in series with the output.
I don't see how this is possible unless the analog out malfunctioned over the weekend while it was off.
I will switch to the other analog out as a test.
As confirmation , the gauges and general obsevation agree that the output is not on.
I switched to the other analog out.
The only program change is PQW752 to PQW 754.
Works just like it did before.
What could have happened to take out the first output? Everything is still functional, nothing is shorted out, there has been no release of magic smoke.
Maybe it is just one of those things, but at this level in my S7 game , I always suspect that the problem is more likely something I did.
I don't see how programing could cause an analog out to fail though, it wasn't even on.
All PLC hardware in this example is only a few weeks old and has less than 20 hours run time on it. In the lab, 75 deg F, regulated 24 volt DC power supply.
I wonder if this is common with the 313C?
This will not be good if they fail so easily.
Well, it seems it is possible to latch the analog out.
During my tests I discovered when I switched the output , all seemed to work , so I went back to the edits I had been doing when it failed.
And it failed again.
Hmmmmmm, prolly not hardware.
I must have been writting over the output somewhere.
Not sure where.
The big negative to the FC and FB structure is, when you discover one little error , you spend a long time saving and re entering all the variables to every instance of every effected block. And then the block that it is used in.
Not likin that bit.
Not likin that bit.
You don't need to do that. I'm not sure what you mean by "one little error", but if you are talking about adding or removing parameters, you can just right click on the call and select "Update Block Call". Or, to do everything at once, you can do a block consistency check (Blocks>ConsistencyCheck>CompileAll).
But I'm not sure what you're doing. The whole point of using FCs and FBs is so you don't have to go back and change every one.
ah Ha...........
I thought it should be that easy.
Now it is much better than before.
"What I was / am doing" is this:
I write a FC and or a FB and then call said FB from OB1.
Then several days later, I get new information that makes a change in the original FB or FC necessary.
SO I edit the FC or FB and save it.
Then when I save OB1 the block(that has just been edited) is red.
Then I go to the new block and install the new block in the old blocks place and move all the external parameters over.
Now I have only had to do this a couple times, but it is anouying.
I thought there was a better way............just wasn't sure where or what it was and didn't want to stop to ask at that moment.
Thanks,
Let me begin with a few general details. I am new to Step7 I have read as many posts here about PIDs as I could. I do not find an answer to my...
5,171
I am now gettign closer to what I hope to be the end of this project. The last bit to tackle involves a couple basic issues. 1) I have oil being...
20
7,143
hi... i have an issue in s7 300 plc, while we run the machine(in idle there is no fault) , plc cpu goes in SF mode, after restart the power cycle...
124
Dear experts, I have the following setup: CPU-313C (6ES7313-5BF03-0AB0 V2.6) + CP343-1 (6GK7343-1EX30-0XE0 V2.0) communicating with Siemens PC...
2,707
Hello Every one I am trying to connect the encoder with siemen's 300 plc but dont know how to do it... Could some one send me the connection of...
2,207