3G3RV omron inverter
I know nothing about that particular inverter. But if a 3 phase then
Hook motors in parallel on VFD output - all 3 phase of course and all the same voltage and best if all the same size.
VFD must equal (Kw) the total of all motors Kw
The VFD has overcurrent but that is for TOTAL load
- not each motor-
each motor should have overcurrent protection and some means of disconnecting it if overloaded. In my mind each overload would have a switch that would tell VFD to stop and also set an alarm light to know there is a problem.
All motors must start together - you cannot add motors to running VFD and motors.
One thing to watch out for is how long the cables are between motor and VFD. READ the VFD factory manual.
Do NOT run the motors too slow say below 10 or 5 Hz the motor fan may / will not run fast enough to cool the motor.
I think that should cover basics.
Dan Bentler
Hello all, Im using modbus to communicate to an Omron 3G3RV drive. Im trying to use parameter A1-03 to initialize the parameters to the user...
3,856
Has anyone done SMS messaging from an Omron CJ2J-CPU31 PLC? If so could you help please. Omron here in Oz have not had any experience doing this...
138
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
63
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
100
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
256