4-20mA analog output from DCS
sat
Jan 2024
India
I need to read three 4-20mA signals from a DCS(ABB) in a remote 6 channel analog input module with RS485 modbus port.
When I connected the three signals individually i can read the raw count values in my AI module,
but if all the three signals connected simultaneously all the three signals stops working in the module.
Is there any alternate way to connect all three signals in a single Analog input module?
Thanks for your help.
This is a classic common mode ground loop situation.
The ground reference for the AI circuits in the AI module is at a different potential than the ground reference at the DCS AO. The AI module has a common mode limitation which is not exceeded when a single AO signal is connected but the common mode limitation is exceeded when the all 3 are connected.
In rare cases, floating the DC (-)(removing the connection from (-) to ground) of the power supply powering the AI module (DCS) will solve the problem.
Once and only once, I discovered that the AI needed a ground connection to the AO unit.
The usual approach is to buy 4-20mA isolator modules.
Gents I'm working on a small project here and the customer requested to control the drive with 4-20mA by using Micro820 Analog output 4-20mA...
6,079
Hi Guys, I was given a task to configure using level setpoint to have an output of 4-20ma equivalent using GE Fanuc 9070. Is this possible? If...
2,050
Dear All, I want to use a 4-20mA output from Omron AO module, so I did the following configuration: PLC used CJ1M-CPU22, rack 00 CJ1W-AD041, rack...
4,969
Hello, Please i need some help on how to get acccurate values current (4-20mA) at the analog output terminal of controllogix analog output module...
20
9,521
Hi Friends, I have a LVDT for measurement of cylinder stock which output in resistance. How can I connect it to PLC's analog input? If is there...
2,287