cbuysse
Member
It occurs to me that you will want the resistor to be in series with the current load of the loop, and not across the terminals as a shunt. @cbuysse alluded to it in his explanation, but the application is not as straight forward as the OP.
Just to be clear - which terminals are you referring to?
In fact the resistor will (or should) be wired across the terminals for the voltage input on the PLC. There are several ways to go about making this loop work depending on the specific devices involved and existing configuration. I had assumed the OP had already determined the best correct way to wire it and was more concerned with functionality.