5TI to S7-200 conversion

johnsoja

Member
Join Date
Jan 2008
Location
Corbin Ky
Posts
5
I am converting a 5TI to an S7-200. I cannot find any information about a MCR command for the S7-200. Does anyone know if this command is possible with the S7-200? I have searched all the manuals and cannot find anything. Please help clarify.
 
After more research and talking to siemens I have found out that the S7-200 does not have a MCR command. The S7-300 does though. So if you are to rewrite a 5TI program into a S7-200 you are going to have to use a control bit manually, or use subroutines to alter these outputs.
 