hi everybody,

My problem is when the op25 is starting there was a error of " 613 DB error No:101 (0,42) " What is it mean?

Thank you.
 
Hi,

this mean that inside the CPU the data block DB101 is not present,or the data lenght the DB101 is too much small.
The data values (0,42) are refer to the address begin DW0 and the address end DW42.

So in order check the presence of the DB1 in the CPU, if affermative check the data size of the DB (min.42 data word).

regards
 
i have checked the all the data blok in the cpu and there was no such a data blok DB101. My problem is that i have two machine from all of the equipment same but differens between them are product number and the date. One of them erase its plc memory i wasn't have its s5 program so i upload the other machine plc programs than download the erased one. Both of them same plc same op everything is same.

If i upload Coros op25 program from right one, i can download it to esared memory machine. But how, I do not know. I have no Comtext or protool. furtermore i have no op25 program. I need the upload its program by using flash memory card on its ic such as EPROM M27C1001-12F1. How it is possible to the that?
 

Similar Topics

hi i need help my pv 550 is connected through 1761-net AIC+ to micrologix 1500. problem started with falut light on microligix 1500 and lost...
Replies
2
Views
2,634
Hello, Received pop-up message on PC, saying I must restart CP (our PC has CP5613/CP5614 card) to continue work. Also such info, in same error...
Replies
1
Views
1,582
Hello Folks, I have a PanelView 550 kepad/Touch. Its communicating to a Micrologix 1500 PLC via DH-485. After running the auto cycle for a while...
Replies
4
Views
11,528
The system archetecture: panel view550 conected to a AB SLC 5/03 via DH 485. The panel view indicate error code 613"Required network node not...
Replies
7
Views
11,431
Hi guys, I have one SLC50/3 that connected to a Panelview1000 with DH-485 communication between both. But when the SLC50/3 go to RUN mode, on the...
Replies
5
Views
15,315
Back
Top Bottom