A little help

joeparrish

Member
Join Date
Nov 2007
Location
owensboro ky
Posts
161
Ok I am new to panel veiw programing I added a screen The same as I have on a few others and had no issues the screen Just has a few indactors and, a go to screen on there.

It downloads and all screen work fine but this one I click on the screen from the main screen takes me there but says (613 required network node not found) then I have to power down to get out of that screen

The Panelview is a allen bradley 550 cat 2711-t5a5-L1
The Plc is a allen bradley micro logix 1500 LRP series c
using panel builder 32 to program

Thanks
 
Check the links (data) on that screen in your tag editor and make sure they are pointing to the controller the PV is connected to.
NodeName.jpg

NodeConfig.JPG
 
Last edited:

Similar Topics

Hello, I am trying to replicate a piece of logic on the PLC5 onto an SEL RTAC. I am using ladder on SEL and FBD. I am having issue on the ladder...
Replies
13
Views
259
I am trying to use pylogix to write to a string array ID_Data_Table_Name. In the array there are 200 possible entries. For...
Replies
13
Views
4,044
Hey guys, I have a client that has a v-notch chlorinator that doesn't run off a 4-20mA loop, it instead has two discrete inputs that drive the...
Replies
6
Views
1,889
Hey all. I need some guidance here. This is something I came across today when a Ref guy noticed that the HMI isn't displaying the correct time...
Replies
2
Views
1,464
i am a beginner plc programmer and have some confusion, a little help would be appreciated . why do we use a normally close contact when we are...
Replies
11
Views
3,161
Back
Top Bottom