A problem with a comparison block

Shohadawy

Member
Join Date
Aug 2008
Location
Egypt
Posts
66
I'm using a comparison block "LE". The block does not generate an output although the condition of the comparison is correct and all the contacts before the "EN" of the block is true. I tried connecting the "EN" directly to the power rail in the ladder but the same problem exists. What may be the cause of such problems?
 
What may be the cause of such problems?
A "double-coil" - reusing the same output BELOW the comparison block, where another rung turns off the output. Remember that the PLC will do what it was LAST told to do.
 