ab 5/03 fault, slot 00 cfg?

ebrakespin

Member
Join Date
Oct 2009
Location
mn
Posts
2
Im very new to this and my work has made me in charge of it :oops:. I had a service guy call and tell me a machine in the field has been faulting with what he said "slot 00 cfg". I think this machine uses a dtam for the interface. The cpu has been changed out as well as the rack to eliminate those as the culps.

any help on what this fault error means or how to fix it would be greatly appreciated!
 
New info,

the error code is 0056h. The dtam users manual says this is because 'The rack configuration specified in the user program is incorrect'.

So is there any other reason this would fault other then having a bad rack or the wrong rack?
 
There was probably a problem in the connection between the CPU card and the rack which prevented it from properly identifying the rack itself. It may be that just reseating the CPU may have fixed this.
 
The SLC-500 controllers are very careful about the integrity of the I/O modules in their chassis, and they check at startup and often during runtime to be sure they're all working. The controller will fault if it can't talk to an I/O module, because it considers the system to be out of control when the I/O modules aren't working.

Any error code "5x" in the modular SLC controllers uses the last digit to designate the slot number of the module at fault.

How many slots is your backplane ? Anything special in Slot 06 (the controller is Slot 00).

This mechanism isn't perfect. If there is a general problem with the chassis or the backplane interface from the CPU, it can blame the last module in the system. If you have a 7-slot chassis and are getting error 0x56, it's possible that you have a bad chassis (though replacing it tends to rule that out) or a bad interface between the SLC and the chassis. Noisy power and poor grounds can also result in this error code.
 

Similar Topics

Good morning everyone I’m currently working on a omron device net and have a nord drive that fell off the network. I have limit knowledge in...
Replies
0
Views
27
Hi. We've been asked to do an upgrade on plant, consisting on a PLC upgrade. This involves replacing a 1747-SDN module to a 1769-SDN, in a network...
Replies
0
Views
59
in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
4
Views
145
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
94
hello I am getting a 57h fault - Specialty I/O module has not responded to a lock shared memory command within the required limit. Fault randomly...
Replies
2
Views
105
Back
Top Bottom