MartyMaucher Member M Join Date May 2014 Location Pensacola Posts 91 Oct 30, 2015 #1 Well, I don't see why these CMP and MOV instructions are not active. I understand the bManZeroAOut input can be misleading if it gets turned off somewhere else, but I even put a jumper across it and still got no results. Any ideas?
Well, I don't see why these CMP and MOV instructions are not active. I understand the bManZeroAOut input can be misleading if it gets turned off somewhere else, but I even put a jumper across it and still got no results. Any ideas?
dginbuffalo Member D Join Date Dec 2010 Location Buffalo,NY Posts 630 Oct 30, 2015 #2 Are your sure that routine has a JSR block in the main calling it out?
MartyMaucher Member OP M Join Date May 2014 Location Pensacola Posts 91 Oct 30, 2015 #3 That was it... I knew it had to be something silly. You guys are going to make a PLC programmer out of me, yet.
That was it... I knew it had to be something silly. You guys are going to make a PLC programmer out of me, yet.
dginbuffalo Member D Join Date Dec 2010 Location Buffalo,NY Posts 630 Oct 30, 2015 #4 MartyMaucher said: That was it... I knew it had to be something silly. You guys are going to make a PLC programmer out of me, yet. Click to expand... I speak from experience...
MartyMaucher said: That was it... I knew it had to be something silly. You guys are going to make a PLC programmer out of me, yet. Click to expand... I speak from experience...
daba Lifetime Supporting Member D Join Date Jul 2004 Location uk Posts 5,401 Oct 30, 2015 #5 What version of Logix Designer are you working with?