Hey guys,
I have a quick question about connecting a PanelView Plus to a Micro850 using the RS-232 port on both devices.
Originally I had the Micro850 connected to a PanelView Component, and from my understanding both of these were "DTE" devices, so a null-modem cable (1761-CBL-PM02) was used to connect them.
Unfortunately it seems like the PV+ is a "DCE" device, so the null-modem cable won't work for connecting it to the Micro850. Looking around, it seems like the 2711-NC21 cable would meet this requirement.
I'm just posting this for verification that my understanding is correct, since I'm piecing together information from a bunch of sources and I'm having a hard time finding official documentation backing any of it up.
Thanks