AB PanelView Plus to Micro850 (RS-232)

lolproe

Member
Join Date
May 2013
Location
Canada
Posts
11
Hey guys,

I have a quick question about connecting a PanelView Plus to a Micro850 using the RS-232 port on both devices.

Originally I had the Micro850 connected to a PanelView Component, and from my understanding both of these were "DTE" devices, so a null-modem cable (1761-CBL-PM02) was used to connect them.

Unfortunately it seems like the PV+ is a "DCE" device, so the null-modem cable won't work for connecting it to the Micro850. Looking around, it seems like the 2711-NC21 cable would meet this requirement.

I'm just posting this for verification that my understanding is correct, since I'm piecing together information from a bunch of sources and I'm having a hard time finding official documentation backing any of it up.

Thanks
 
Sorry for the double post, but I have some information to add.

I got off the phone with my local AB distributor, and they only have the 1761-CBL-PM02 cables available right now so I can't get my hands on a 2711-NC21/2 in the short term.

It seems like my only option at this point is to get a null-modem adapter. I'd like to start testing soon, so I found the following adapter and could get it delivered by tomorrow.

http://www.digikey.ca/product-detail/en/2708753/277-2408-ND/2529024

This looks like the right thing for this application, but if anyone else could take a look at it and confirm my thoughts that would be great.
 
You're on the right track.

I like those low-profile null modem adapters, but any unit from a general purpose electronics store like Radio Shack will work.
 

Similar Topics

Hello I have to implement an Ethernet/IP communication between a micro850 PLC (2080-LC50-24QBB which is supposed to have Ethernet/IP...
Replies
6
Views
9,772
Hey guys, I'm in a pretty weird situation and I'm looking for some input. Without going into too many details, I need an Allen-Bradley Micro850...
Replies
4
Views
12,031
I'm at a loss here and hoping someone else has seen this: Background: We've got two identical machines on our floor (we'll call them machine A &...
Replies
0
Views
48
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
100
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
78
Back
Top Bottom