AB PLC 2/30 upgrade suggestions needed

Cogen

Member
Join Date
Apr 2010
Location
Bayonne NJ
Posts
9
I have a PLC 2/30 that I need to start getting some thoughts togather on upgrading. I am leaning towared a SLC 500/5 as I have RSLogix 500 and I have four of those on site so it makes since for me to keep them all the same. If this is not a good idea let me know.

What would I need in the way of hardware and software conversion etc to do this project successfully? I hear that AB offers new IO cards for the PLC 2 rack that would interface directly to the SLC. Should I go this rout or just rip out the entire old PLC 2 and put in a complete SLC 500 system?

Thanks for the help
 
My answer depends on how many I/O you require. ?

If I/O count is under 80 I would consider a Micro Logix 1100.
If I/O count is under 144 I would consider a Micro Logix 1400

If the I/O count is higher again I would consider Compact Logix or Control Logix

Unless you already have a spare Slc 5/05 you would find the above to be cheaper, and it is also the direction that Rockwell appear to be directing for new installations hence the pricing.
 
I agree with Gil. I would stay away from the SLC not that there are problems,but because ther are applications that make these a good choice.

We need an I/O count , rack size and layout. Before we can give much advice.
 
Be careful with MicroLogix as there may not be online edits depending on the one you pick. A 1500 is on several machines at a customer site and it takes nearly 5 minutes to download the program in stop mode, all to change a constant or flip a NC to a NO. I hate them.

The SLC platform is on the way out judging by Rockwell pricing and intentions. It's a shame because it is a great software platform and bulletproof hardware. We continue to install them for customers with an installed base for the reason you said - consistency. However the CompactLogix platform is something you should take a serious look at.
 
ML1100 and ML1400 do online programming and have Ethernet comms,
this has made them a popular option, on Rockwell sites.

The ML 1000,1200, 1500, DO NOT have online programming or Ethernet comms built in.
 

Similar Topics

Hello all, I have a one problem. I would like to upgrade Mitsubishi PLC Q02 to Q03UDVCPU. I have Q02 program and I change to PLC type and try to...
Replies
7
Views
164
Hi everyone, Kind of new at this, so we recently upgraded our 1769-l32e to the newer 5069-L320erm, i converted the file over and Verify the...
Replies
8
Views
417
I'm involved in upgrading an IDEC FC5A-D12S1E PLC to a FC6A-D32P3CEE. I've attached the original layout of the system. Since then, another HG3G...
Replies
0
Views
449
Hello, I've recently tried to upgrade my PLC controller from a L72 to L84ES and everything seemed to work, all buttons and screens as far...
Replies
9
Views
2,643
Hi, we are using 1756-L61 PLC redundant system in one location . due to some minor faults , we upgrade the firmware from 19.52 to 20.58. after...
Replies
1
Views
1,343
Back
Top Bottom