Hello, all I am hooked from an idec PLC to PF 400 Drive and need to read and write data via modbus rtu over rs485 I got it all hooked up correctly but its been 2 years since I had a scadapack hooked to 3 of these drives and talking and cannot remember the addressing. PF 400 has Address (Decimal) 8192 for writing logic commands but what is that in modbus? Stupid question I know, but I dont remember how AB uses their parameters and how to read and write to an address like that. And now I am using a different type PLC.
When the PowerFlex 4-series user manuals refer to "Registers" they mean Modbus Holding Registers, which are commonly referred to as "40000x" registers because old Modicon controllers prefixed a "4" to the Holding Register memory.
So Register 8192 (decimal) is "48192" in Modicon addressing.
More specifically, you will use Function Code 0x06 (write Single Register) with offset 0x2000 (hex) = 8192 (decimal) to write to the 16-bit Command Word.
Appendix E of the PowerFlex 400 User Manual is the best reference to keep handy for this.
Yea ive been up and down the manual i was just wondering about their decimal addressing i guess 8192 = 48192 or 48193? since idec is offset buy one i believe.
Yeah, the 0 vs. 1 offset thing is a notorious issue in Modbus.
In the PowerFlex 4-series drives, "register 8192" is based on the first register having an offset of zero. 8192 decimal = 0x2000 hex, so if you looked at the Modbus data in a serial analyzer you would see "20 00" in the Offset field.
If you're dealing with a controller that considers an offset of zero to be "Modbus Register 40001", then the Command Word is "48193" and the Speed Reference word is "48194".
how can i communicate with powerflex 400/40 through arduino with the help of modbus rtu/tcp. what is modbus register mapping of powerflex 400?
1,712
Hello I am a newbie so apologies in advance if I am not making sense or miss important information. I am trying to setup a PID Loop on a...
6,280
Hi All My issue is with an MSG error code 37 - 'Message timed out in local processor' between an ML1400 and 8 Powerflex 4M's. When the VSD's are...
8,925
Evening all, Can someone please tell me (i know the manuals say it is possible), if MicroLogix 1400 PLC will communicate thru 1763-NC01 cable to a...
8,555
Hello I have a powerflex 400 of 25HP for a 60amp 25HP motor, the motor have a belt that move the clarifier of milk. It is a process that requires...
4,201