I want to start/ stop a motor during certain hours of the day using the clock in a SLC5/03 cpu (1747-L531 OS302)... example: I want the motor to turn on between 0400 and 1600 hours
Do I monitor the S:40 bit in an EQUAL TO/ GREATER THAN instruction or is there a better way to do it?
I won't say it's better, but ... if you're not familiar with the LIM (limit) instruction, you might want to take a look at it. The Test value will be the S:40 (real-time clock hour) that you mentioned. Just watch out when entering the value of the High Limit (turn off time) or you might get an unexpected extra hour of run time.
And while you're experimenting with the LIM, pay careful attention to what happens if the value of the High Limit is LESS THAN the value of the Low Limit.
I need help with having the real time clock trigger an event everday at 1:00 A.M excep the weekend. I do not have an HMI screen. This is not a...
4,243
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
91
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
103
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
104
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
96