AB SMC Flex motor controller fault

diat150

Lifetime Supporting Member
Join Date
Mar 2006
Location
Louisiana
Posts
1,475
hello all,

a customer of mine is getting a line loss B fault code on their motor controller, model number 150-f135nbd. he was telling me that the voltage is high on the incoming power from the electrical company, over 500 volts. supposedly when they switch over to their onsite generator, that runs around 480, they dont have any issues. It sounds like an issue with the power company... but im not a high voltage electrical guy and I dont have much experience with motors and motor controllers.

Just wondering if anyone can give me some advice so that I can lead him in the right direction, which will likely be getting him in touch with someone with experience in high voltage.
 
According to the user manual, that fault indicates that the drive is not seeing any voltage on the B line. It sounds like there is a loose connection somewhere between the drive and the incoming service.
 
im thinking more along the lines of it being from the power company. its two different pumps with two different motor controllers. he also told me just now that the utility company did some work down the line and the problem has started since they did the work.

I have him getting with the utility company to get them to come analyze the incoming power.
 

Similar Topics

Hi guys, Been handed a new SNAFU on a job. The MCC what provided with a SMC Flex Soft Starter for a 40hp motor but the motor that was installed...
Replies
11
Views
2,419
I need to purchase a few Large soft starters for our plant and we prefer to stay Rockwell. We have purchased SMC Flex 150 in the past and they...
Replies
7
Views
182
Hi, I want to start 150 SMC Flex from Studio 5000. I have the AOP and P SMC flex AOI imported in my program. I have also set the logic mask to...
Replies
0
Views
329
Hi there, very much new to AB Drives / Drives in general. Driving a pump with SMC Flex Drive Rating: Pump (5-135) Revision 6.008. Currently the...
Replies
6
Views
2,169
Dear experts, I have encountered an SMC Flex (361A,480V) wired for 3-wire where that if you press 'Start' Then immediatly press 'stop' it will...
Replies
7
Views
1,782
Back
Top Bottom