HI EVERYONE
SMC-3 Allen Bradley smart motor controller failed to start the conveyor motor which has been running for a few years without any problem.
At the moment the system is running without SMC-3 in normal condition,the motor current is balanced and running about 3.5 amps per phase and motor body temperature is normal.
After I received the replacement unit (SMC-3) with the exact type it was connected back into the panel, upon the start up within a few seconds delay RUN/FAULT led came on without any flashing and not energizing the motor.
I took out the new unit out of the panel, wired up and tested on bench (wiring diagram attached). The result the same as before even though I increased the start time by setting dip switch . I wonder if someone can tell me if the unit could be defective even though it is brand new unit.this is basically an electronic contactor and it should power up the motor when 3 phase voltage and control voltage (110 ) applied to unit. Just to remind you dip switches (1 to 16)set based on original set up. Thanking you all for your time.

SMC-3.jpg
 
When the LED is steady and nothing happens, but you KNOW for sure it has all 3 phases getting to it, that usually means the dip switch that selects the motor configuration, #15, is in the wrong position. If you wired that starter and motor as shown in that drawing, sw# 15 must be in the "Line" position, or "I" (up), not "Delta" or "O" (down). If its in Delta but you connected in in Line, it is thinking you have the motor connected wrong.
 
Thanks jraef your suggestion worked. I am just curious about dip switch #15 because my documentation states that dip switch #15 off: normal and on : up to speed on page 2-5 of publication 150-AT001B-EN-P April 2002.
Regards Perspolis
 
Are you using the manual from the old one that you removed, to interpret the newer replacement unit? The switch numbers may have changed. The manual I looked at shows Sw #15 as the mode selector.
 
Hi jraef
Thanks for clarification,I have downloaded the dip switch setting description which is totally different. Thanks again
Regards Perspols
 

Similar Topics

First ithought that it works like vfd, but it doesnt. How it works then?
Replies
1
Views
2,924
Recently, I was involved in a problem with peak intensity at startup of a water pump. This pump was pulling over 50 Amps on 120 Vac/ 1 phase...
Replies
13
Views
16,860
Good Morning , We have a 100 HP , 480 V (Full Load Amps 124 ) Hammer Mill motor that has a Wye/Delta starting procedure. I would like to put...
Replies
16
Views
4,260
Does anybody have experience using a Prosoft MVI56E-MCM module and a ebmpabst W3G910-KV12-61 (or similar) fan motor? The Modbus register list...
Replies
4
Views
1,611
I have a 20hp/460VAC/60Hz motor on a SMC3 soft starter. I have used several of these in the past on previous projects. I have had them go bad in...
Replies
7
Views
4,947
Back
Top Bottom