AB VFD Troubleshooting
chintankAne
Apr 2014
Surat
80
Hi I am working on old machine in which AB controllogix PLC used.
VFD : Power Flex40 (22B-D6P0N104)
VFD connected to PLC using Eathernet
3 Phase Induction Motor : Rating 3 HP full load current 6 Amp.
I check and found problem in my VFD and I have spare VFD the detail of that VFD is as follow
Spare VFD : Power Flex4 (22A-D8P7N104)
I can connect my spare VFD ????
If Yes then
I need to change in VFD configuration in my PLC?? HOW??
http://postimg.org/image/hgdzumket/
The PowerFlex 4 VFDs do not support Communication Cards. So, the only way you could make it work is if you have some Digital Outputs, Inputs, and an Analog Output available.
Then you would have to modify your PLC Code to use those instead of the Ethernet Communications.
Stu....
Another potentially big issue is that the PF40 is capable of Sensorless Vector Control, the PF4 is not. Most of the time if an application did not need SVC, then they would have used the less expensive PF4, so it's a good bet that they used the PF40 because they needed to. Replacing it with the less capable drive could lead to poor performance or failure of the machine.
Thank you for your help
I check and found I have Spare PowerFlex 40(22B-D010N104) drive as well. So i decided to go with power flex 40.
So while changing drive model what change should I need to change in contrologix PLC(Program).
I think you're mistaken. I'm sure the Powerflex 4 VFD can be used on Ethernet, DeviceNet, Profibus & ControlNet using comms cards. See here http://www.ab.com/en/epub/catalogs/36265/1323285/9566682/Accessories.html
Technically, you are correct, but the PF4 would not be a drop in replacement for the PF40, as other items would be required to make it work. From your AB Link, and the notes under the Communications Options.
§ PowerFlex 4 & 4M drives require External DSI Communication Kits. Communication Adapters cannot be drive mounted.
I was aware of this, because I have dealt with this issue before. Hence the reason for my answer to the OPs question.
Stu....
Our fan VFD keeps faulting out about every hour. To rule out a bad motor, I disconnected the motor wires from the VFD. After that, the VFD runs...
2,302
Hey guys, so I have a VFD 70 controlling a fan. It's been running fine for some time now and no modifications have been made recently. It has been...
2,978
I'm trying to troubleshoot a machine tonight and am running into the limitations of my VFD and 3-phase motor knowledge, and hope you good folks...
20
6,315
Recently read "Motor (VFD) Testing Tip With the increase in use of Variable Frequency Drives (VFD's), and increased machine uptime expectations...
4,719
I am not an electrician, but like all of us, are sometimes required to be one when troubleshooting a VFD. Does anyone know of a good reference...
6,312
DaMan
D