Dear All,
I have build and HVAC control system for a big shoping mall, based on ABBs AC500 and using the CS31 bus.
The air handling units (AHUs) are split into two groups.
Each group has an AC500 PM573-ETH CPU and 7 RIOs (CI592) on CS31 bus.
Each CS31 network is about 600m so a repeater from phoenix contact was used in the middle of the bus. The cable used is a profibus cable and it is properly terminated at each end (R1->B1 & R2->B2). There are no VFDs around nor any other equipment that would produce electrical noise.
The system was commisioned (without the repeaters) and it seemed that all is ok but after a few days the client copmlained that the system is down. I visited the site and I read the errors from the PLC. The problem was that the PLC could not see the RIOs through the CS31 bus. On the RIO modules(CI592) the CS31 LED flashed indicating that the module is in diagnosis mode. The problem only went away after a power cycle of each RIO. I left and the system failed again after a week or so. At that point I thought that the problem was the bus length exceeding the mark of 500m. So today I went on site and installed the repeaters thinking that this was the root of the evil. The repeaters worked straight away without any issues. I left and then after a couple of hours I get a call from the client that the system cannot see two of the RIOs.
I asked him to reboot them and the problem went away.
In the past we did that 1000 times with Siemens & profibus and had no issues whatsoever. The ABB rep convinced us to give the AC500 a test drive but now it pays us back with hard time.
As you understund I am in the spot and at the moment I dont know what the problem may be. So any help is highly appreciated.
Regards Nik
I have build and HVAC control system for a big shoping mall, based on ABBs AC500 and using the CS31 bus.
The air handling units (AHUs) are split into two groups.
Each group has an AC500 PM573-ETH CPU and 7 RIOs (CI592) on CS31 bus.
Each CS31 network is about 600m so a repeater from phoenix contact was used in the middle of the bus. The cable used is a profibus cable and it is properly terminated at each end (R1->B1 & R2->B2). There are no VFDs around nor any other equipment that would produce electrical noise.
The system was commisioned (without the repeaters) and it seemed that all is ok but after a few days the client copmlained that the system is down. I visited the site and I read the errors from the PLC. The problem was that the PLC could not see the RIOs through the CS31 bus. On the RIO modules(CI592) the CS31 LED flashed indicating that the module is in diagnosis mode. The problem only went away after a power cycle of each RIO. I left and the system failed again after a week or so. At that point I thought that the problem was the bus length exceeding the mark of 500m. So today I went on site and installed the repeaters thinking that this was the root of the evil. The repeaters worked straight away without any issues. I left and then after a couple of hours I get a call from the client that the system cannot see two of the RIOs.
I asked him to reboot them and the problem went away.
In the past we did that 1000 times with Siemens & profibus and had no issues whatsoever. The ABB rep convinced us to give the AC500 a test drive but now it pays us back with hard time.
As you understund I am in the spot and at the moment I dont know what the problem may be. So any help is highly appreciated.
Regards Nik