Hi hoping someone can assist me with current issue I am experiencing with an ABB drive.
Problem I’m experiencing is a ABB drive supply a large fan cannot reach 100% speed without tripping on supply loss with no fault indication.
I have 2 drives operating exact same spec fans and only get issues with one drive when it has been off for extended periods no issues with other drive.
When ramping from 98-100% drive will trip, I have tried everything code traps, service support ABB, changed hardware. Annoying thing is sometimes drive flukes it and will reach 100% and as drive is running non stop once it hits 100% it stays that way until next maintenance outage! I’m currently running drive at 98% after maintenance period.
I am at a loss and if any experts could assist it would be hugely appreciated
Unfortunately not, ran at 95% for 24 hours then attempted ramp to 100 same issue.
I agree very weird and zero answers from ABB service team.
May you add more details?
VFD nominal power, nominal input voltage, power supply type (direct to grid/tansformer/etc), acceleration ramp time?
Motor nominal power/nominal speed?
So, VFD cut output voltage without any message when try to increase speed above 95% of what? Nominal motor speed / max reference frequency set on VFD / or any other speed?
The obvious answer if it is tripping on supply loss, is that it looses the supply! With a centrifugal fan that last 2% increase in speed will mean the drive pulls a chunk more power. See the Third Fan Law in the link below:
Log the supply voltage over the fan speed range.
Members of this forum helped me out a great deal a couple of years ago with a question I had regarding acceleration during torque control of...
4,411
I am getting an AD1_PLACE1 fault on my drive and am stumped, any pointers would be appreciated!
1,885
I am using a ACS800 regen drive to drive a 500hp motor for a engine dynomometer application. I am currently running the drive via ethercat...
1,698
Hi All, We have a ABB ACS 800 Drive, Have 2 AO for RPM and current output. As default setting, both are available on X9-12 terminal. I am...
2,248
Dear team, i need to run ABB ACS800 two drives in master follower mode.Im using ABB RDC0-03C option kits with fiber optics lines. As they...
2,371