Hello,
As the Topic says i'm having a strange fault code on my ACSM1.
The inverter controls a conveyor in a steak machine. It is controlled as a slave unit, I got another M1 that is the master (which is controlled over profibus from a Siemens s7-314C-2PN/DP system).
The machine was FAT-tested in Sweden for 2weeks without any problems.
Now when the machine is installed on-site ( in another county in europe ) the installer getting a fault code as you can see in the picture.
If you read the manual for the ACSM1 the fault code says;
Incorrect input power and motor
cable connection (i.e. input
power cable is connected to
drive motor connection).
And the solution to the problem is ;
Check input power connections.
You can bypass the fault code by entering (0) in paramter 46.08.
I wanna know why this fault is here and why we dident saw it on the FAT-test.
The electrical cabinet where shipped with the machine so all the cable connections was still intact when the cabinet left Sweden.
Has anyone experienced this before?,
Sorry for a long thread, thanks in advance,
osman, according to the installer the phase position is correct. Yes the fault is there when the vfd is powerd on.
badger,the supply voltage is in the specified limits from the electrical specifitions the cabinet was constructed from
you need communicate the commissioning engineer to check the external problem,
since the FAT have done but not SAT.
check list form must observe.
whether disconnect any cable go to motor side than power up again.
isolate the internal and external problem.
Thanks for the help all, the problem was solved last week 2014-10-17.
The fault was that the installer had clamped the motor cable and caused an shortcircuit.
Thanks all for the fast help,
Best regards Victor
Hello, Another super problem to solve. Rockwell has discontinued the panel view and now we need to use the panel view plus. When converting the...
2,588
hi all, I have an VFD ABB ACSM1, i have many problems with this Drive: I dont found the option to reset the Encoder. The option "New Custom...
2,403
Hello All, I have an ABB drive type ACSM1. Does any one know the part number of its control panel? is it standard control panel or not? and can it...
3,076
Quick question: Can PLC ABB PM554-T generate PWM/PTO for controlling servo drive? Can not find manual file.
57
Recently we have purchased the Rosemount 752 remote indicator to replace with new one, Capability file for that FF Device is unable to import with...
57