ABB inveter cannot reverse

TheVo

Member
Join Date
Jun 2005
Location
Ho Chi Minh City
Posts
24
Dear all

I have one problem with ABB (ACS 800, i do not remeber clearly) inveter.
Forward :It was running but when I run with reverse the motor cannot run.
Parameter 10.01 :EXT1
10.03 :REQUEST
Anybody help me to correct it

Thanks
Phung
 
Check Parameter 2001 and 2007. Minimum speed and frequency is defined as maximum speed NEGATIVE. So, for example, on an ordinary 1800rpm motor set to run full speed in both directions, you will need -1800 in 2001 and/or
-60Hz in 2007.

This is a common difficulty with ABB drives but is does have advantages.

Let us know if this is the problem.
 
The last time I set up a ACS 800, in order to get it to run the motor in reverse, it seems like I had to place a jumper from 24+ to an input on the terminal strip. I think it was a reverse enable, but not sure. Sorry, I don't remember the terminal #, but the manual should show it.
 

Similar Topics

does anyone have an install or know if/where i can download it for the following "ABB PS501 Control Builder Plus V2.3 " the software was a free...
Replies
2
Views
116
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
167
Hi hoping someone can assist me with current issue I am experiencing with an ABB drive. Problem I’m experiencing is a ABB drive supply a large...
Replies
4
Views
225
Hello all, I have an ABB PLC (PM573) and it has without MC card. I need to take backup from PLC to PC (in automation builder v2.7 ). My...
Replies
10
Views
473
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
Replies
1
Views
199
Back
Top Bottom