My plc is S7-200 CPU226+EM231 AI2×RTD,when connect to Pt100 all is OK,i.e. when the temperature is 30 ℃,the data AIW0 is about 300(I use the channel one).but when I change Pt100 to Pt10000,the dip switch setting to 11011001,according to the EM231 RTD manual,the data AIW0×0.1=temperature value ,but now the data AIW0×0.1≠temperature value ,why?
thanks Damir
when the temperature is 37℃,the data AIW0 is about 920,when temperature is 85℃,the data AIW0 is about 2200;
When changing DIP switches,I have turn power on/off several times,
this sounds strange.
There are multiple dip settings for the different PT1000 types.
Did you measured the resistance of your PT1000 at a defined tempreature and compared with his datasheet?
Maybe you had a PT100 with a different alpha value.
Otherwise i would try a another module if applicable or change this one.
not PT1000,I think it's PT10000(α=0.003850?) ,because when temperature=25℃,the resistance is about 10K Ω ,I have changed another module and new one PT10000,the result is the same.