Absolute parallel encoder to standard DI-card
Plc_User
Dec 2005
Belgium
317
Someone advised me that it would be no problem to connect an absolute parallel encoder to a standard di-card, because the delay time of the di is only 5 ms and absolute encoders in many cases don't move fast.
Has someone experience with this? If so, how do you do conversion if it is gray-code?
If I want to use a dedicated card (Siemens S7) which one should I use then?
Thanks.
I don't know Siemens, but make sure that if your card is updated asynchronously to the program scan that you could get invalid values without special instructions to avoid have the PLC read a value while the encoder is in the middle of strobing in new data.
I believe with Controllogix, the CPS instruction takes care of that, but I will defer to the Siemens experts to help you decide whether your Input card will be synchronous or not.
With PLC-5 and SLC local Inputs a standard TTL or DC input cards work fine with the MVM (masked move to get only the position bits if less than 16 bit resolution), along with the code examples MichaelG posted.
In OkiePC's example it would still be an issue. He is referring specifically to the Allen-Bradley Logix platform. With this platform the I/O is not updated at the end of the program scan. It is updated based on a time set in the module configuration. This can cause the state of the I/O to change at any point in the program scan. In you case that could mean in the middle of the Gray Code conversion logic.
It's been a while since I used a Siemens PLC product but I believe that they all do I/O updates at the end of a scan. In that case you wouldn't have this problem. But that is something you need to check first.
Keith
In case of asynchronicity, just before the conversion, copy an image of the input bits, if addressable as a complete word into an internal word which can be used bit-by-bit.
I have 2 Absolute Encoders 8192 steps per Rev. (Model TR Electronic CEV65m-11003) These Encoders communicate to the PLC5-60 via Parallel push/pull...
1,522
I may have something coming up that uses a multi turn absolute gray code to binary, parallel interface encoder. I do know how to convert the...
18
11,434
Hello. An absolute encoder on a rotary axis gives values in range -2147483648 to 2147483648. When value is > 2147483648 , the encoder value is...
20
2,322
Hello, First thank for all the help i've gotten through this forum over the years reading others threads. I'm having an issue with Kinetix 5700...
5,958
I have an application that needs 20 inputs and 20 outputs with only 10 XNOR and 10 NAND blocks. I could do it with relays, but this could end up...