i could use some help with this one.
I've been round and round with siemens AND modem manufacturer.
i'm trying to connect to an S5 115 PLC remotely via modem.
according to siemens documentation, you need a pair of modems that support 11 bit mode. they suggested Multitech ZDX modems.
i bought 2 of them.
they gave me a doc that is supposed to tell me how to do it with the multitech modems, but it doesn't work.
i get PLC timeouts when trying to go online.
i've been through their instructions step by step numerous times over the past two months, changing init strings, etc. all to no avail.
has anyone done this? can you help me figure out what is wrong?
i need the modem connection to be transparent, 11bit.
i've got a current loop adapter in line between the modem and the PLC, and i can go online fine when connected directly to it.
somewhere along the modem transmittion it's stripping control characters or reverting out of 11bit mode. but i can't track it down.
at the moment i'm sniffing the RS232 traffic coming out of the PC directly, and comparing it to a capture that was taken from the rs232 port coming out of the remote modem.
i can tell it's different already. but i can't tell how, yet.
I've been round and round with siemens AND modem manufacturer.
i'm trying to connect to an S5 115 PLC remotely via modem.
according to siemens documentation, you need a pair of modems that support 11 bit mode. they suggested Multitech ZDX modems.
i bought 2 of them.
they gave me a doc that is supposed to tell me how to do it with the multitech modems, but it doesn't work.
i get PLC timeouts when trying to go online.
i've been through their instructions step by step numerous times over the past two months, changing init strings, etc. all to no avail.
has anyone done this? can you help me figure out what is wrong?
i need the modem connection to be transparent, 11bit.
i've got a current loop adapter in line between the modem and the PLC, and i can go online fine when connected directly to it.
somewhere along the modem transmittion it's stripping control characters or reverting out of 11bit mode. but i can't track it down.
at the moment i'm sniffing the RS232 traffic coming out of the PC directly, and comparing it to a capture that was taken from the rs232 port coming out of the remote modem.
i can tell it's different already. but i can't tell how, yet.