Adding a remote IO rack for 1756-L61

SingerChemE

Member
Join Date
Feb 2007
Location
Dayton,Ohio
Posts
16
I will be adding rack of remote IO under a 1756-L61 and I am wondering what are my options? I have a 1756-DHRIO module already in the rack with my processor using ch A for DH+ communication.

The client would prefer to use a controllogix rack for the remote IO....can I simply place a 1756-DHRIO card into the remote rack and use channel B to connect via RIO to the rack containing the PLC?

I have no more space in the rack that contains the PLC.

Thanks in advance!
 
Does the existing rack have any other communication modules?

ControlLogix doesn't support RIO between CLX racks.
 
You could use PointIO with an ethernet adapter, or a CLX rack with an ethernet card. You'd need RSNetworx for Ethernet to schedule.
 
Your options for connecting 1756-series chassis to a ControlLogix controller are ControlNet and EtherNet/IP networks.

Since you already have a 1756-ENBT, the simplest mechanism would be to use another 1756-ENBT in the remote chassis. RSNetworx for EtherNet/IP is not required. If your existing 1756-ENBT is connected to your plantwide or enterprise network, you will need to be certain that your switch and network support IGMP Snooping and IGMP Querying.

Ethernet technologies and basic layout are covered in the Rockwell Automation publication "EtherNet/IP Modules in Logix 5000 Control Systems", publication number ENET-UM001.

Another option is ControlNet, which requires 1756-CNB, -CNBR, -CN2, or -CN2R modules in both chassis. RSNetworx for ControlNet software is required to create the network schedule. ControlNet has the advantage of not requiring special switches or powered elements in the network, and delivers repeatable and precise performance, but does require specific software tools and some familiarity with the technology.

ControlNet configuration in ControlLogix systems is described in the Rockwell Automation publication "ControlNet Modules in Logix 5000 Control Systems", publication number CNET-UM001.
 

Similar Topics

adding new AI to PLC5 as remote IO team, it will be great if some one help me on this. I have a PLC5 controller...
Replies
6
Views
5,232
Hi, I need help adding a new interlock switch to an existing circuit. I have never done on the existing circuit. I did set it up on the...
Replies
0
Views
24
Hi all I’m looking at adding a RFID card reader to comfort panel pro , how do you set the rfid up can you connect to existing users and password...
Replies
0
Views
51
Hello all! So I have one project with a S7-1214 and a MTP1500 "Project1" and one project with another S7-1214 "Project2". Both of these PLC:s need...
Replies
6
Views
116
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
94
Back
Top Bottom