adding expansion card to micrologix 1400

skippy83

Member
Join Date
Feb 2013
Location
tennessee
Posts
2
Last night I tryed adding a 1762-OW16 output card to a Micrologix 1400 PLC. I was unsuccessful. If I tryed to read I/O configuration it would not see the expansion. If I picked the card from the list and downloaded, it faulted out that the I/O did not match. I looked up the card on the AB website to be sure it is compatible, and it is. The PLC is less than 6 months old. I also tryed a different card but it had the same results. Does anyone have any info on this problem?
 
Welcome to the forum Skippy. This might seem like a trivial question, but is the ribbon cable from the module plugged properly into the base unit with no bent pins? This connection can sometimes be a bit tricky and many a technician has had difficulty keeping the connector seated as the modules are manipulated during assembly.
 
Yes it is plugged in properly. I removed and plugged back in several times. I also made sure the pins was not bent. I couldn't come up with anything wrong with the ribbon cable or plug. I debated on changing the processor, thinking maybe the plug on it was bad until i found out it was not that old
 
Been a while but isn't there a requirement to have a termination end cap after the last expansion module? If so, do you have one? I seem to remember without one, the processor won't see the expansion module. 1769-ECR I believe is the part number.
 
The termination endcap is only required for the Micrologix 1500.

It's a long shot but try this: Go to the I/O Configuration and click on Adv Config for the suspect module. Make sure the Series number matches what's printed on the label, and try turning on the "Ignore Configuration Error" checkbox.

P.S. What versions of RSLogix/RSLinx are you running?
 
Last edited:

Similar Topics

Hi First post here! I admit I am not too used to handle interrupt OBs in Siemens. I have a customer who has been buying a standardized solution...
Replies
4
Views
258
Hi all I’m looking at adding a RFID card reader to comfort panel pro , how do you set the rfid up can you connect to existing users and password...
Replies
0
Views
47
Hello all! So I have one project with a S7-1214 and a MTP1500 "Project1" and one project with another S7-1214 "Project2". Both of these PLC:s need...
Replies
6
Views
114
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
91
Hello, Im building project with 1756-L82ES controller and 1756-IB16S card but i cant find it when trying to add the card to IO configuration...
Replies
3
Views
166
Back
Top Bottom