Dear All,
I need help to sort out some issue i am facing ,
i wanted to read the data from the device that has modbus communication protocol . and i wanted to read that data through compactlogix L32E processor so i can use that for other simulation purpose in programs .
How i can achieve this ?
Is there separate modbus module need to add in AB compactlogix PLC so it can read from other device data ?
please help me
 
For ModbusRTU, if you want it for some simulation purpose, as you mention, you can check AB sample code library site and write modbus, there is an application there. If you really need to make application, which will control anything, I would go to third party device, like others mentioned above.

If you are talking about ModbusTCP, L32E doesn't support it directly and you need third-party device anyway.
 
If you need an HMI, or you are willing to switch an existing HMI to a Red Lion, then I will cast another vote for that. I normally don't like to put an HMI in the middle of a control mechanism, but I have trusted even the lowly Kadets to do just that. They boot faster than some PLCs and are highly reliable and excellent protocol converters.

Another method I have seen is to use a Micrologix 1400 as a gateway. This can make sense if you need to use it for more than just a data collector.
 

Similar Topics

Hi all I’m looking at adding a RFID card reader to comfort panel pro , how do you set the rfid up can you connect to existing users and password...
Replies
0
Views
22
Hello all! So I have one project with a S7-1214 and a MTP1500 "Project1" and one project with another S7-1214 "Project2". Both of these PLC:s need...
Replies
6
Views
106
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
83
Hello, Im building project with 1756-L82ES controller and 1756-IB16S card but i cant find it when trying to add the card to IO configuration...
Replies
3
Views
159
Hello, I have a pair of redundant 1756-L71 controllers rev 24. These controllers currently have produced and consumed tag interfaces to 3 other...
Replies
2
Views
182
Back
Top Bottom