Adding v23 to existing Studio 5000
So, v21 should be discarded by the incompatibility problem?
Do you recommend to install v23, v24, v28, v29, v30 in this order (Win7 64)?
I give service for 2 plants of the same group and I need at least this versions.
Best Regards
Installs have to be in order from the oldest version to newest one. You will have to uninstall newer if you need older versions added and reinstall newer.
If it were me, I'd install v20.04, v21.03, v23, v24, v26, v27, v28, v29, v30 in that order.
v20.04 will bypass all compatibility issues with PLC's running v20
v21.03 will not bypass the compatibility issues in PLC's running v21, but by now everyone should have updated their software and PLC's to v21.03, so you've got a better chance with that than v21.01
v23 and upward have no known compatibility issues (at least, of the type previously discussed)
You *can* install the software packages in any order up until you hit v30 - but yes, good practice to install them from oldest to newest.
And if you are going to install v30, make sure you disable the "start page" from loading by default on the previous versions. Something with the v30 install will cause them to fail to start if the start page tries to load. That tip is buried in the v30 release notes somewhere.
Hello all! So I have one project with a S7-1214 and a MTP1500 "Project1" and one project with another S7-1214 "Project2". Both of these PLC:s need...
83
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
77
Hello, Im building project with 1756-L82ES controller and 1756-IB16S card but i cant find it when trying to add the card to IO configuration...
145
Hello, I have a pair of redundant 1756-L71 controllers rev 24. These controllers currently have produced and consumed tag interfaces to 3 other...
176
I'm adding an IAI Gateway with 2 axes connected to it. To an ethernet network on my PLC. So, I think the math is correct on the Input and Output...
150