1. I have NO problem using Controllogix to a Rexroth controller by setting up a generic E-net module with
Input Assy Instance = 100, size=1 DINT (4 bytes) &
Output Assy Instance = 150, size=1 DINT &
Config Assy Instance = 01 , size=0.
2. A Micrologix1400 was setup with MSG & CIP Generic to Rexroth, similar to the above setup, MSG was sent & done normally without ANY errors, however I don't see any data. see picture below.
[I can create an error by putting in a diff. instance number, for ex. From what I can see, the setup looks correct, the read msg was sent to controller, but not receiving it for some reason]
3. However, If I put both Controllogix & Micrologix on at the same time, then the Micro start receiving data from the Rexroth controller.
ADQ101 [Another Dump Question]. Help . Thanks.:=)