HI EVERYONE: help help help
I did configure RSLINX AB_DF-1 and followed the instruction manual for 1747-UIC. Cable 1747-CP3 connected to slc processor and UIC ports RS232 and little black switch set to RS232 port
but the slc processor not visible on RSLINX.
I have some question in reference to AB tech notes:
1 the processor port must be configured for DH485 and not DF1.
2 Avoid duplicate node addresses. For instance, make sure that the processor node address is not set to the default node of RSLinx, which is 0. Thanks
I did configure RSLINX AB_DF-1 and followed the instruction manual for 1747-UIC. Cable 1747-CP3 connected to slc processor and UIC ports RS232 and little black switch set to RS232 port
but the slc processor not visible on RSLINX.
I have some question in reference to AB tech notes:
1 the processor port must be configured for DH485 and not DF1.
2 Avoid duplicate node addresses. For instance, make sure that the processor node address is not set to the default node of RSLinx, which is 0. Thanks
Last edited: