Allen Bradley Analog Scaling
Jothiswarup
Apr 2014
Somewhere
33
Hello everyone
PLC -1769-L33ERM
Analog Card - 1769-IF4
Input Range - 0V to 5V
Data Format - Engineering units
Scaling required - 0 to 1000
So can I just divide [Analog input value/5] ? or am I doing something wrong here?
Thank you.
I don't know what you're doing. Have you configured the module? Does it return a number of 0 at OV and 1000 at 5V? If so, then you may do whatever you wish with the data. Divide, Multiply, Add, Subtract... Whatever.
Yes I did configure the module to the above mentioned values. It has been running for a day and seems to be scaling correctly. I am just making sure. Thank you.
The 1769 series analog modules have a less complex configuration than the 1756 series analog modules.
You don't specify the Min/Max Engineering Units scaling values, and there are no Clamp values or Rate Alarms or LL/L/H/HH Alarms.
Instead, when you select "Engineering Units", and 0- 5V range, you get values between 0 and 5000.
The full range of the module is -0.5 V to 5.25 V, so you could actually see values between -500 and + 5250.
This is in Table 3-7 in the Compact I/O Analog Modules User Manual, publication 1769-UM002.
Hey Folks. I know its the same old struggle, but I need to get Analog Inputs into an AB system without any Analog Input Cards. Initially I...
5,538
Hello to all. I am new to PLC’s as well as this forum so if I make any mistakes please forgive me. I am having an issue using the 2080 OF2...
2,812
Hi, I'm curious if anyone has made a master sheet or cheat sheet for all allen bradley card's analog inputs/outputs? As much fun as it is to...
1,599
This hasn't become my problem yet, but it may soon... Ancient PLC-3 (yeah, I know) has been humming along for decades. It now has some analog...
2,467
Hello all. I have been working with an SLC 5/04 system, which houses various Digital and Analog INs and OUTs, up to Slot 29. I am currently...
2,533