Hello all, is it possible to reset a faulted armor block thru the plc? I know I can reset the devicenet card, and some devices thru the PLC, but I have not found anything about resetting the armor block using logic in the PLC. Thanks in advance.
Is it an ordinary ArmorBlock, or an ArmorBlock Guard safety I/O device ?
Do you know the sort of fault that the ArmorBlock is experiencing ? Is it a communication failure, or a diagnostic fault on the I/O side ?
Many communication failures require a power cycle, but diagnostic features are generally resettable via the Output data assembly or a CIP explicit message.