Short answer is maybe. It all depends on what comms module you have in the drive, and how the drive is configured.

Will.
 
You will need a 22-COM-C communication adaptor for the drive to connect to ControlNet. But if the host is a PLC-5, you will not be able to download parameters to the drive, only read them from the drive.
 
Please specify the PLC and the intended method of connecting to the drive.

If your PLC is capable of MODBUS communications then this is possible.

And please don't repeat your posts. Stay with the original thread.
 
Last edited:
Our shop only has 1 1203-usb adapter
I was hoping to set an aic and use "connected component" to downlad parameters to powerflex 4 drives if we have to change a drive out
 
No - the 1203-USB adapter provides communications using the DH485 protocol either with RS232 or RS485 electrical interfaces. It cannot do what you wish.
 

Similar Topics

An issue occurred at an organization here in whereby the ControlNet card developed a fault. Card Details: Catalog/Series; 1756-CN2RXT B Part No...
Replies
0
Views
450
Hey Everyone, I need to Interface Ignition SCADA ethernet network to an Allen Bradley SLC5/04 Serial RS232 DF1. Has anyone out there found a low...
Replies
4
Views
1,006
Good morning all, I've got a customer in a bind. They, like many, got confused about Allen Bradley's EtherNet/IP protocol and assumed it was...
Replies
10
Views
2,675
We have a lot of POINT-IO modules in various places all over our machines. Occasionally one of the daisy chained cables between our 1734-AENTR...
Replies
4
Views
1,724
We have many sites with PLC-5s and 1785-ENET sidecars that are being pounded pretty hard by the GE IGS driver (Kepware) and iFIX/Historian...
Replies
1
Views
986
Back
Top Bottom