Do you already have this module running in your system, or are you setting it up for the first time ?
First, the tag you describe is not a Boolean "bit" format; "Local1:I.Ch0Data" it must be an integer or floating point value.
Please explain specifically what kind of module that data comes from, and folks can help you understand its data type and meaning.
Prosoft MNETx modules have an internal "database" that is a simple flat one-dimensional table of integers. Users configure the module to "map" sections of that database to ranges of Modbus addresses.
Your first task is to determine which section of the database is represented as Modbus "Input" registers (the ones that are denoted with 1xxxxx).
The Prosoft example code and user manuals are really pretty good.