Allen Bradley + Prosoft Tag ReadOnly

ptcjoe27

Member
Join Date
Oct 2019
Location
Makati
Posts
5
Hi All,

Good day.

Just want to know if you all have an idea on how to convert a Bit address (Local1:I.Ch0Data) from Allen Bradley to Modbus Address 10**** using Prosoft MNETC.

Thank you in advance. :geek:

Sorry newbie here..

Thank,
Joe
 
Welcome to the PLCTalk forum community !

Do you already have this module running in your system, or are you setting it up for the first time ?

First, the tag you describe is not a Boolean "bit" format; "Local1:I.Ch0Data" it must be an integer or floating point value.

Please explain specifically what kind of module that data comes from, and folks can help you understand its data type and meaning.

Prosoft MNETx modules have an internal "database" that is a simple flat one-dimensional table of integers. Users configure the module to "map" sections of that database to ranges of Modbus addresses.

Your first task is to determine which section of the database is represented as Modbus "Input" registers (the ones that are denoted with 1xxxxx).

The Prosoft example code and user manuals are really pretty good.
 
Hi Ken Roach,

Thank you very much for your reply.

Sorry for the wrong choice of word. It is "Boolean" and not "Bit".

The prosoft will be installed next month. I just want to prepare it today :oops:

I also follow the instruction manual of prosoft but the example is only a float/real.

Anyway. Thank you very much again for your reply Ken.

1.png
 

Similar Topics

Hey guys, I'm working on a proposal for a client, and long story short I need to suggest a new master PLC for polling existing RTU sites that are...
Replies
23
Views
9,876
Hi how's it going. Was just wondering if someone could help me out. Recently one of the guys over on the LinuxCNC forums put me onto getting an...
Replies
13
Views
125
Hello, Does anyone have one of these cables and willing to open the case so I can see the cable connections inside? 2707-NC5 I have sourced the...
Replies
3
Views
76
Currently trying to find: micrologix ethernet interface 1761-NET-ENI AIC to micrologix 761-CBL-AM00 Ser C cable These are used for micrologix...
Replies
3
Views
129
in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
4
Views
172
Back
Top Bottom