SCADA design varies widely, so I can't say there's any one right way to design yours. There are definitely Forum users with current knowledge of the "state of the art", especially with IP radios. A system with 75 remote stations is pretty big and deserves some serious consideration.
But I can mention things I know don't work well !
First, the MicroLogix 1100 and 1400 are great controllers for small remote stations, but I would not use one as a central data collector or SCADA master for a system with more than a handful of nodes.
The MicroLogix online editing feature has an important exception: you can't do an online edit of a rung with a MSG instruction in it. If you are adding nodes as the system grows, you're going to need to stop and download to the master controller every time you want to change the communications routine. This becomes tiresome fast.
You also mentioned that the system will grow, up to 75 nodes. If you are using TCP/IP then you're going to run into a TCP connection limit on the MicroLogix 1400; it can create just 16 outbound TCP connections.
Even the SLC-5/05 will run into this limit: the 1747-L553 has the highest limit, and it can create 60 outgoing TCP connections.
You would need to go to a ControlLogix with a 1756-EN2T to get enough TCP connectivity for your whole system (the 1756-EN2T can create 128 TCP connections).
If you use a SCADA computer to communicate with the remote controllers directly, PC operating systems typically don't have such low limits. Windows XP, for example, had a limit of 10 simultaneous incoming TCP connections, but not practical limit on outgoing connections. A proper server operating system like Windows Server 2008 can make many hundreds of outgoing connections.
I'm going to leave the SCADA supervisory software selection as a separate topic, but I'll warn you that most salesmen and even technical guys (including me) don't have deep experience with low-reliability networks. The drivers and configuration are meant for good-quality 100 MB Ethernet, not for a licensed radio network. The credo of anyone working with wireless communications should be "we can deal gracefully with packet loss", not "PING works, so there's nothing wrong with the radios".
In my experience, Kepware is very good at handling networks that have frequent packet loss, with features like "polling demotion". RSLinx Enterprise (the preferred data source for FactoryTalk View SE) is very good at integration with ControlLogix, but it assumes a fast, high-quality connection. Even though it means some extra labor creating tag databases, I would choose KepServer over RSLinx Enterprise for a SCADA system OPC server.
Many Forum users will emphasize the importance of separating the business or enterprise network from the automation network, and this is absolutely crucial for a wireless network. The SCADA systems I've worked on that have persistent, years-long battles with their telemetry have one thing in common: the telemetry network is connected carelessly to the enterprise network with unmanaged Ethernet switches.
That's principally an expression of their casual approach to the automation systems, but it's also a source of some of the problems. I've run Wireshark on these systems and found streaming audio protocols, printer discovery protocols, router discovery protocols... all kind of stuff that both the radio system and the remote PLCs had to deal with.