Allen bradley SMC flex no load trip fault#40

Firoj_aga

Member
Join Date
Apr 2017
Location
Rourkela
Posts
3
Motor running for 2 hours, when load is reduced then it is tripping in no load.
We want to run the motor irrespective of loading condition.
Kindly suggest for the same

Fault 40: no load tripping.


Hence how to avoid no load fault
 
Smc flex 150
motor flc: 360amps

sometimes it runs 4 hr.
But whenever loading is reduced to minimum it trips in no load

we want to run it without load also
 
What that fault really means is that there is >25V votlage drop across the SCRs during starting (or soft stopping). It's the result of a pre-start check, so you will not get this fault if the motor is running / coasting because the bypass contacts will be closed.

So the usual cause is that something is opening and re-closing your start / run command, which tells the starter to re-start, but because the motor is regenerating there is a greater voltage difference across the SCRs. So the first thing to check is actually your control system, as in something is "bouncing" or chattering. A voltage fluctuation >15% in your control power will do it too.

If you have anything on the load side, such as a load isolation contactor or a 2 speed contactor setup, that contactor opening and closing will do it too.

If you have an external bypass contactor, not just the internal one, you need to have programmed the starter to tell it that, otherwise that might cause this too. But I'm pretty sure it would do it all the time, not just sometimes. Sometimes is usually a clue that it's a control circuit issue.
 

Similar Topics

RSlinx has become unrelable when we have many plc's talking through it so we are trying to implement wonderwares built in I/O server. we changed...
Replies
0
Views
2,980
Last week we had two issues with two different refrigeration compressor contactors. They are wye-start delta-run motors with contactor controls...
Replies
17
Views
11,366
Currently trying to find: micrologix ethernet interface 1761-NET-ENI AIC to micrologix 761-CBL-AM00 Ser C cable These are used for micrologix...
Replies
2
Views
3
in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
4
Views
160
Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
14
Views
443
Back
Top Bottom