Allen bradley ultra 3000 digital servo drive

kwjamme

Member
Join Date
Sep 2014
Location
wisconsin
Posts
2
Fault E10 displayed, book says excessive regeneration of power. dont think thats the problem. any other ideas? motor drives a right angle gearbox with output to a shaft and chain driven.
 
Have you tried all of the remedies listed in the manual? Has this error suddenly appeared after months of acceptable operation or are you just starting it up for the first time?
E10 is bus overvoltage. It is generated when you try to decelerate the load too fast. To be able to decelerate a large load rapidly, you may have a braking resistor installed. The suggestions in the manual are related to checking those aspects of the operation of the drive.
 
Thanks and you are correct, a downstream roller had bad bushings and was causing the roller that was driven by the 3000 drive to have jerky operation.
 

Similar Topics

Hello everyone. I am working on a rebuilt AB-Ultra series drive (1998) and the firmware for the drive is needed to test and use the drive. I would...
Replies
0
Views
457
Needing RS Logix 5 programming examples for communicating (PLC 5/40E) to multiple Ultra 100 servo drives over devicenet. The user manual for the...
Replies
0
Views
1,309
servo sürücüm var. kodu: 1398-pdm-030, lütfen çok acil bir programa ihtiyacım var
Replies
6
Views
3,913
i have servo drive. code : 1398-pdm-030 , I need a very urgent program please
Replies
0
Views
1,403
Hello everybody, need your help, I have old piece of equipment with Ultra 100 drive, and have one spare drive on shelf. I want to program spare...
Replies
4
Views
4,282
Back
Top Bottom