Analog Input 1794-IF4I over DH to PLC5/40
abs014000
Jan 2007
TX
Hi all,
I have a current transducer set up on a motor wire providing 4-20 mA output into a 1794-IF4I module. The wiring seems good thus far, but I'm developing the logic. Since the PLC rack goes over Data Highway to a 1771 rack, I'm stuck with scaling the input in RSLogix5. Here is the problem:
We have a BTR set up since all I'm interested is the current feedback from the motor wire. In the BTR block, I set up the Data file to N7:0 (seeing that the input will be a range from 0 - 32,768). Now, when I look at my N7 data file, in N7:5 I see "-32768". I'm not sure why it's a negative value and why bit 5.
Ideally, I'd like to scale the value I'm getting from 0 - 5 Amps. I have the calculations I need to perform, but have to get past this data reading.
Any suggestions/advice?
Thanks.
Firstly, you must be communicating over RIO, not DH.
You have to configure the module by sending data via BTW.
You can do this the hard way by studying the manuals and creating the necessary data files and program. Or, you can let RSLogix do it for you - enter the module in the processor's I/O configuration, double-click on it, then fill in the blanks and let RSLogix create the ladder rungs - all pretty painless.
Dear Members; We have Fluke 754 hart communicator. We have wired up three transmitters of Rosemount Model C3051 with this input module. But when...
1,861
Could someone show me an example on how to wire the analogic input for lets say channel 0 ?? Ive found this manual...
5,245
Hello all Nub here, i am working with a 1756-L61 clx5561 controller rev 15.3 I have a 1794 IF4I on node 38 of my DNET configuration. I want to...
3,089
Dear , problem : Adding and configuring analog input module 1794-IE8 to existing running system SLC 5/03 through 1747-BSN (DH485) System: - 2...
3,771
Hello All, Have any of you experience of using Allen Bradley Flex 1794-IE12 analogue input cards? In particular with signal cables greater than...
3,516