Could anybody fetch me an idea how to make analog input 0-10v to control preset of a timer in ML1000-ML1200 (with slc500 I move SCP scaled output to PRE TON ) thanks
lost in time
thanks 93lt1 didnt know until now that ML1200 comes with SCP instruction , my rslogix and manuals are outdated , any way ML1000 still doesnt have SCP instruction and I still wonder what is the best way to handle analog input to timer preset in ML1000
The SCP instruction simply solves the equation,
Y = mX + b
where Y is the scaled output.
X is the input (analog input) value.
b is the value of Y when X is zero.
m is the slope of the line,
also equal to (Max Y - Min Y)/(Max X - Min X)
If your Micrologix doesn't have the instruction, you can roll your own.
Similar Topics
I'm having a hard time wrapping my head around this today. Very likely due to being sick and not thinking straight, plus my inexperience with...
Replies
18
Views
8,372
Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
Replies
1
Views
34
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
Replies
5
Views
126
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
Replies
5
Views
135
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
30
Views
1,190
Back
Top Bottom