Boolean -> Integer conversion for 90-30
denman_100
Dec 2007
Winnipeg
Is there a boolean to integer conversion for the GE 90-30 PLCs? I want to determine how many fans are running, (%I1 - 20). I was going to convert each input to a 0 or 1, then add them up to determine how many are running. Right now I have 2 rungs for each input, one to move a 0 into an variable or a 1 into that variable depending on the value of %I1 for exmample. Is there a more efficient way of doing this?
There is no instruction in the 90-30 function set to count the number of bits set over a range. You will have to roll your own routine.
Her is a possible rutine:
First create a DWORD variable with address %I0001. Then AND that variable with hex 000FFFFF. This will let you use the other twelve inputs elsewhere in your program.
Move a zero into a register to be used as an index. Also move zero into your "Number of Bits" register.
Use the "LABEL" instruction to create a target for a "JUMP" instruction.
Use the bitwise shift right instruction to shift the bit pattern of the DWORD variable you created earlier. If a "1" gets shifted out, add 1 to "Number of Bits".
Unconditionally add 1 to the Index.
If the Index value is less than 20, JUMP back to the LABEL.
Be very careful with the JUMP instruction when JUMPing to a rung earlier in the ladder logic. If you make a mistake and get stuck in the loop for longer than 200 milliseconds, the PLC will crash on a "Watchdog Timeout" fault.
Hi, I need to decode the integer value to boolean and store the each bit of 16bits in different variable of boolean type and to be used in the...
2,465
Hi, I need to decode to the integer value to boolean and store the each bit of 16bits in different variable of boolean type and to be used in the...
3,457
Have beginner knowledge of digital controls, and intermediate/advanced knowledge of socket clients and listeners (written logging proxies, socket...
3,785
Hi, I am trying to convert an array of Booleans into an integer so that I can use it to display a message on a SCADA system. I have looked on...
22
16,755
Hi. I haven't touched an Allen Bradley PLC for more than 10 years and I'm kind of rusty. I want to do something really simple in a FBD section...
862