Can I use the g.input command with Mitsubishi IEC Developer V7
deeside
Jul 2004
I am trying to read data from the buffer of a QJ71C24 serial port (Ch1 - RS-232) on a Q PLC. I have got as far as attempting to use the G.INPUT command to retrieve the buffer data but cannot seem to find it in the list of functions. As the rest of this PLC was programmed using IEC I do not want to use GX Developer (Which does have the G.INPUT command). How do I use dedicated instructions within IEC Developer?
Cheers,
Deeside
Hi Panic Mode,
Thanks for the reply.
I am already aware about the instruction g.input in the SH(NA)-080006 manual but that only appears to describes how to use the command in Gx Developer. My problem is I want to use the instruction in Gx IEC Developer which does not seem to have an equivalent function for g.input.
Cheers,
Deeside
I assume you checked the two manuals that come with GX IEC Developer?
And you can retrieve data from buffer memory with U\G addresses or TO\FROM instructions too.
Thanks Crossbow,
I contacted my distributor and he suggested the same and I have now successfully retrieved the buffer contents using the FROMP command. I cannot find any reference to the G.INPUT function in any GX IEC documentation and conclude IEC v7 does not support the G.INPUT function.
Hello I m using Unity Pro XL. I want to scale my analog inputs. I configured the Analog Input Module as 0-4 mA and 0-10 V . What is the way...
3,006
Hello! I have made some program my siemens S7 200 plc (Check attachments) And i try hadle that I0.1 whit Weintek HMI panel, but i do something...
3,576
Hi All Using RSLogix 5k ver 15. I've created few phases as follows main . . . Phase:Cooling . . Phase:Heating . . In ver 15 you can...
1,670
Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
23
627
Hello All, After trying to transfer some field changes on the safety scanner microscan3, and verifying, the device is stuck at .... waiting for...
92