Can you inhibit a RS5000 module with logic
PLC_Shaggy
Aug 2010
Indiana
I am in the process of migrating a SLC to a CompactLogix. To aid this conversion I am using a AENTR to make the SLC a remote rack to the CL while doing my development. The problem I am running into is there are several vision cameras. For the SLC to work I need to Inhibit the cameras in the CL. I would like to be able to do this in the logic by monitoring the status of the AENTR. If the adapter is active I take control of the cameras. Once the adapter is in fault (not being used), I inhibit the communications with the cameras with the CL.
I have tried using the SSV command. But for Modules, I only get a Mode selection. This toggles the 'Major Fault On Controller' setting.
For now I will just manually toggle the Inhibit Module setting.
Thanks for any help.
Yes you can you need to use an SSV.
You need to send 4 to the Module Mode.
For Example
Module Name: Camera1
Variable: Camera1SSV
Rung:
XIC InhibitCamera1 ONS InhibitCamera1ONS Mov 4 Camera1SSV SSV Module Camera1 Mode Camera1SSV
If you then want to enable the module you move 0 to the Mode.
It's better practice to read the mode using a GSV first, and then set/reset bit 2, and then send changes mode using SSV. The other bits may have separate functions that you may not want to change. If bit 0 is set, a major fault will be generated if the module connection faults while the controller is in Run mode.
Is there a way to change inhibit state of an IO card at the bit level? I know it can be done with modules via GSV/SSV But can it be done on...
3,564
Question- Say I have 8 digital INPUTS to my PLC, any of which may be asserted HIGH for a few seconds, all these inputs "OR'd", currently, to...
3,556
My customer has a PLC-5/80 with 20+ RIO racks. They've asked me to remove one of the racks without shutting the system down. Can I set the...
3,998
So everyone knows how to inhibit a module in studio or rs5000 I need to do the equivalent in tia portal 15. Need to run some test code but my...
2,522
Good afternoon to all, I have a 1756-EN2TR PLC using studio 5000, along with a Kinetix 6500 (2094-EN02D-M01-S0) drive. This drive controls my...
4,349