CE Conformity - protective earth cable to enclosure's removable panel

matt_sd

Member
Join Date
Jan 2007
Location
Australia
Posts
96
Hello everyone.

I have a question that is regarding CE Conformity as CE mark is required for any product sold in Europe.

Now I know that if a panel had mains voltage, the door has to have a protective earth grounding cable to the door as if the live comes loose and touches the panel door, the breaker will trip saving someone from getting electrocuted if they touch the door.

Now we are going to mount a electric motor in an enclosure, this enclosures has a removable panel. Under CE, does this need to have a protective earth cable from the panel to the earth?
I assume it doesn't as the motor has its own terminal box and the lid of the motor terminal box would have an protective earth cable already.

Everyone agree?

Thanks

Matt
 
As I see it the removable panel has to be grouded also.

If we assemble a switch panel witch has removable panels( eg covers for cable infeeds) we always ground every panel with 6qmm ye/gr wire directly to a common ground rail.

Brgds.
 
I use the serrated mounting nuts included with the cabinets I buy to mount the sub panel to the mounting studs. Since the nuts are serrated, they bite through the powder-coat and make a solid ground connection. Also, since equipment such as drives, power supplies, and PLCs require connections to a ground, I run those to a common grounding bar attached to the side of the enclosure. This insures a star ground point and minimizes the possibility of ground loops. Doors are grounded with a wire because one can't rely on the hinge to maintain ground continuity.

As to CE cert, I'm not sure, but separately grounding the subpanel couldn't hurt. It's a belt-and-suspender approach, but the additional cost - a piece of wire and possibly a terminal lug - would be minimal.

-rpoet
 
All metal parts need to be grounded, so you will not only have to ground the enclosure but also any doors and removable panels.
 
thanks for your replies everyone,

just to confirm our situation:-
a 3 phase cable will come into the terminal box mounted on the motor, the cable is glanded at the motor terminal box. The wires are terminated at the motor terminals. The motor terminal box (that comes with the motor) has a lid that will have a protective earth once the lid is attached, there are no live conductors visable at all in the once the lid of the terminal box is sealed.

Then there is a enclosure that we will put over the motor (for acoustic reasons). This enclosure is in 2 parts, a removal top section and bottom section.

Now this looks a different situation from an electrical panel that would have live connections when the panel/enclosure is opened up. Do you know if our enclosure would require a protection earth?
Thanks

Matt
 
Last edited:
I would call this a mechanical cover and not an electrical cover. I do not see it much different than an access plate on a machine. Therefore it would not require bonding (grounding) to the motor driven unit framework.

However if there is any doubt it will not take that long nor that much cost to do it. I have seen cases where static problems may have been cured prevented with a simple bond.

Dan Bentler
 
It doesn't matter what's inside. All metal parts need to be grounded. BTW, how does the motor cable get to the motor in the first place? Surely it's brought into the enclosure somewhere. Imagine if something happens to the gland.
 
There is a large open slot in one side of the enclosure, the motors cable will come in there as well as some hydraulic pipes (the electric motor has a pump on it to create hydraulic power).
 

Similar Topics

We broke the glass on the new PanelView Plus 7 .... 2 months after the install. Our vendor stated that we cannot buy the repair parts...(Touch...
Replies
5
Views
207
I have a problem writing to the remote control zone to trip the Sepam 80 module via Citect. I am able to connect to the Sepam 80 and read other...
Replies
1
Views
3,261
Hi guys, I'm working on a project and the client request us to supply them a EMO with a transparent protective cover (PVC)? Our EMO (XB5 AS542)is...
Replies
0
Views
1,484
I would like an opinion from pannel builders if you use or not Residual current protective devices in your control pannels. Thanks
Replies
14
Views
5,926
Is there anyone familiar with GE LM10 protective device? I tried to connect to this device using AB DeviceNet scanner 1756-DNB. I could not get...
Replies
0
Views
2,342
Back
Top Bottom