If I post a .cxp program that controls a centrifugal separator, would someone be willing to take a look at it and tell me what memory address I have to alter to change the analog output that changes when the shoot_relay is energized? As a guide, the value of the output changes from 88% to 100% when the "shoot" is initiated during CIP? I'm not at the location, but I have someone there that can change the value. It's a 48-rung program and should be pretty easy to decipher for an Omron guy...
 
There are no values in the memory area. Do you have any *.mem
files associated with the project file? Possibly D21, D100?

Here is the program ladder file in pdf format.
 
Thanks for the reply. I'll contact the site. I assume they can use cx programmer to view the memory file.
 
From the I/O table, it appears the analog module is unit 0, so the addresses associated would be 2000 - 2009.
It would be helpful to know the complete module number.

D9 is moved to 2001 and D10 is moved to 2002 in rung 37 and 38 in section 1. Values are being moved into D9 and D10 in the rungs above. You will need to trace that logic back to verify where the values are actually being set.

Hope this will help.
 
From the I/O table, it appears the analog module is unit 0, so the addresses associated would be 2000 - 2009.
It would be helpful to know the complete module number.

D9 is moved to 2001 and D10 is moved to 2002 in rung 37 and 38 in section 1. Values are being moved into D9 and D10 in the rungs above. You will need to trace that logic back to verify where the values are actually being set.

Hope this will help.

D10 was the memory address we had to change. It's MOVed into Y:2002. learned a lot about Omron PLCs in the last 24 hours...

Thanks for your help.
 

Similar Topics

Hello , I want copy a changing value from analog input to registers . I want to do this for example every 1 ms , and store this samples...
Replies
9
Views
4,800
Hi All, I am currently at the beginning of a new project for writing a PLC program (using CCW) for an old sugar centrifugal. Most of our...
Replies
3
Views
2,002
Hello All I am new to the forum and also to the world of PLCs. I would like to have your expert advice, If I can change the floating point value...
Replies
15
Views
5,781
Hello What would be the best way to write a value into "Source B" of a GEQ SLC500 PLC instruction from Wonderware? I would like the operator to...
Replies
2
Views
1,791
I am new to this line of work so please excuse me if this is extremely simple. I have also Searched the forums and web for answeres and am getting...
Replies
1
Views
1,291
Back
Top Bottom